My old thermostat is worn out, so I decided to switch to one of the Sensi smart thermostats. My problem is once I have everything hooked up and I adjust the temp for the AC to kick on, it feels like the fan is blowing but I'm not getting cold air. My old thermostat doesn't require the blue wire while the new one does, but it was wrapped around the wire bundle in the wall so it is hooked up. What could be causing this? My AC is 20 years old, so is it possible that it won't work with the newer thermostat? I've gone through the settings on the Sensi a couple times and everything seems to be set up for my system, but I'm far from an AC expert. Below is a picture of the wiring on my old and new thermostats.
Announcement
Collapse
No announcement yet.
AC Guys - New Thermostat Issue
Collapse
X
-
Your old thermostat was a standard 4 wire hookup. The blue wire you hooked up is probably not hooked up inside the unit. Look at your new thermostat wiring diagram and see if a blue (common) wire is necessary. If it is you will have to find a way to hook it up on the other end. You will need your unit schematic to do this. Be sure you kill all the power and seek help from a professional if you are not comfortable with it.
-
Originally posted by thegrouse View PostYour old thermostat was a standard 4 wire hookup. The blue wire you hooked up is probably not hooked up inside the unit. Look at your new thermostat wiring diagram and see if a blue (common) wire is necessary. If it is you will have to find a way to hook it up on the other end. You will need your unit schematic to do this. Be sure you kill all the power and seek help from a professional if you are not comfortable with it.
Here is a picture of that board upstairs. The blue wire is the bottom.
Comment
-
Originally posted by apc10 View PostI opened the panel on the unit in the attic and the blue wire is hooked up. It was wrapped around the wire bundle in the wall so I just had to pull it out and hook it up to the new thermostat.
Here is a picture of that board upstairs. The blue wire is the bottom.
Comment
-
Originally posted by Chief Big Toe View Postjust looking,,, so the blue is hooked together with the white wire?
Comment
-
Originally posted by thegrouse View PostWhat does the wiring diagram say on the new thermostat? Sometimes there are DIP switches you need to select for you heating/cooling type.
Comment
-
Originally posted by thegrouse View PostDo you have gas heat or a heat pump? Your old thermostat had an O terminal being used, if gas heat it may require the W. Check the wiring diagram.
Where should the white wire be on my new thermostat? I had a W terminal on the old one, but only a W/E on the new one. I connected it to the O/B terminal because it is across from the W on the old thermostat. Should it be on W/E on the new one instead of O/B?
Comment
-
Originally posted by thegrouse View PostNormally IIRC the W is used on gas/oil heat and the O is for a reversing valve. Did the new thermostat come with a schematic? The schematic will indicate how it needs to be hooked up to function.
I did find this online. I'm thinking the W should go to W/E and not to O/B. Could that be the issue?
Comment
-
EDITED:
didnt look closely enough the first time. Yes, you should connect the white wire to W/E for your applicationLast edited by bowhntrmatt; 09-08-2021, 08:06 AM.
Comment