Trying to figure out how many running/ starting amps I need to run my 5 ton central ac unit. Can anyone tell me based off the plate on the unit? I tried google but that wasn’t much help.
Announcement
Collapse
No announcement yet.
A/C running watts
Collapse
X
-
What are you trying to accomplish? If you need the circuit size, use 50a which is the listed max.
Actual wattage will have to be calculated using a volt/amp meter as the fla and rla listed are maximum values, not actual, and voltage varies from home to home. If this is the case, what are you doing with this information?
Comment
-
Then the answer is yes. 17500 / 240 volts is roughly 70 amps. Your condenser is likely drawing 2/3 or so of the max 50 amps per the breaker (just guessing). And your blower fan does not draw many amps.
Before you drop some coin I'd do a more scientific calculation. Get one of these to check the amps. You may need to pull back the flexible conduit to gain access to the hot wires. Check both hots and the higher one should be your amp draw.
But that is a big generator!
Sent from my SM-G973U using Tapatalk
Comment
-
That will run the a/c, it depends on what else you run. If you have a 5 ton a/c you have a pretty good size house (2000 to 2500 sq, ft). I wouldn't count on running any pool equipment, but lights, fridge and a/c should be fine, but no electric heat. Maybe freezer also. I would consider a start relay and capacitor for the a/c to keep the starting time shorter.
Not familiar with Goodman models, is that a heat pump?
Comment
-
I wouldn’t bet on that running your house. Like said above if you have a 5 ton unit, your house isn’t small. It will depend on if your other appliances are gas/electric. Also the generac units are rated lower when running on natural gas vs propane.
For example, I installed a Generac 22kw for my in-laws. It’s only rated for 19.5 on natural gas. They have a 3 ton unit and the inrush while starting their unit almost kills the engine because it bogs it down so bad. We put a hard start kit in the AC and it helped a little.
It’s hard to really know without knowing your whole setup. I would recommend at least talking to a company that installs them and see what size they say you need.
Comment
-
Originally posted by WTucker View PostI wouldn’t bet on that running your house. Like said above if you have a 5 ton unit, your house isn’t small. It will depend on if your other appliances are gas/electric. Also the generac units are rated lower when running on natural gas vs propane.
For example, I installed a Generac 22kw for my in-laws. It’s only rated for 19.5 on natural gas. They have a 3 ton unit and the inrush while starting their unit almost kills the engine because it bogs it down so bad. We put a hard start kit in the AC and it helped a little.
It’s hard to really know without knowing your whole setup. I would recommend at least talking to a company that installs them and see what size they say you need.
Comment
-
Originally posted by double bogey View PostThat will run the a/c, it depends on what else you run. If you have a 5 ton a/c you have a pretty good size house (2000 to 2500 sq, ft). I wouldn't count on running any pool equipment, but lights, fridge and a/c should be fine, but no electric heat. Maybe freezer also. I would consider a start relay and capacitor for the a/c to keep the starting time shorter.
Not familiar with Goodman models, is that a heat pump?
Comment