I am in the process of building a shop and now I have questions on how to power it.
My house currently has a 125amp panel with the meter on the house.
I am getting the powerco to upgrade my service to 200amps and install the meter and 200amp, 8 space panel on the transformer pole.
I will be running the wires after that point.
My question is, what would be the best option to accomplish that?
Option 1:
Run 4/0-4/0-4/0-2/0 Al wire from 200amp panel at the meter to the shop's 200amp panel.
Then run 4/0-4/0-4/0-2/0 Al wire from the feed-thru lugs in the shop's panel to the house panel.
Option 2:
Run 4/0-4/0-4/0-2/0 Al wire from 200amp panel at the meter to the shop's 200amp panel.
Then run 1/0-1/0-1/0-2 Al wire from a 125amp breaker in the shop's panel to the house panel.
Option 3:
Run 4/0-4/0-4/0-2/0 Al wire from 200amp panel at the meter to the shop's 200amp panel.
Then run 1/0-1/0-1/0-2 Al wire from a 125amp breaker in the meter panel to the house.
All of these options would run all cables in underground conduit.
Option 4:
Run 4/0-4/0-4/0-2/0 Al wire from 200amp panel at the meter to the shop's 200amp panel.
Leave existing overhead cable feeding house from pole and connect it to a 125amp breaker into the meter panel.
Which option is best and why?
What wire insulation rating would be appropriate? SER, SEU, URD, etc
TIA
My house currently has a 125amp panel with the meter on the house.
I am getting the powerco to upgrade my service to 200amps and install the meter and 200amp, 8 space panel on the transformer pole.
I will be running the wires after that point.
My question is, what would be the best option to accomplish that?
Option 1:
Run 4/0-4/0-4/0-2/0 Al wire from 200amp panel at the meter to the shop's 200amp panel.
Then run 4/0-4/0-4/0-2/0 Al wire from the feed-thru lugs in the shop's panel to the house panel.
Option 2:
Run 4/0-4/0-4/0-2/0 Al wire from 200amp panel at the meter to the shop's 200amp panel.
Then run 1/0-1/0-1/0-2 Al wire from a 125amp breaker in the shop's panel to the house panel.
Option 3:
Run 4/0-4/0-4/0-2/0 Al wire from 200amp panel at the meter to the shop's 200amp panel.
Then run 1/0-1/0-1/0-2 Al wire from a 125amp breaker in the meter panel to the house.
All of these options would run all cables in underground conduit.
Option 4:
Run 4/0-4/0-4/0-2/0 Al wire from 200amp panel at the meter to the shop's 200amp panel.
Leave existing overhead cable feeding house from pole and connect it to a 125amp breaker into the meter panel.
Which option is best and why?
What wire insulation rating would be appropriate? SER, SEU, URD, etc
TIA