    electrical question

    Looking at replacing my cooktop in my kitchen. I currently have a 30 amp breaker , but I haven't looked if the cable is 8 awg or 10 awg. The cooktop model my wife has decided on calls for a 40 amp breaker.

    In looking at 8/3 romex, it does show that the max amp is 40 amps. The length of run will be pretty short, I would say 15 ft. or less. So my question is do I need to run 6 awg to be on the safe side or should 8 gauge be ok.
    Last edited by wickll; 03-17-2016, 07:49 PM. Reason: clarify

    #2
    No 8 is fine

    Comment


      #3
      #8 will be fine,especially that short a distance. .

      Comment


        #4
        #8 is good for 50 amps

        Comment


          #5
          Most likely your 30 amp circuit is # 10 Before you change the wire out
          check the new cooktop to see if it requires 3 wire or 4 wire
          if it requires 4 wire you need 8-3-w ground

          Comment


            #6
            Originally posted by RDT View Post
            Most likely your 30 amp circuit is # 10 Before you change the wire out
            check the new cooktop to see if it requires 3 wire or 4 wire
            if it requires 4 wire you need 8-3-w ground
            Yes, just checked and old wire is #10, so I will be pulling wire. I haven't ordered it yet, but found in the instructions for wiring to existing 3 wire and to existing 4 wire. But since changing wire, I guess best bet is to go ahead with 8-3-ground. Thanks for the info.