    Electrician Question

    I enclosed a sunroom space between the garage and house to make my wife a gym space. I have run 4 8 gauge wires to a sub panel about 35 feet from my main panel. Will that support 50 amps or just 40? It really wont matter, just a curiosity. I am installing a couple of plugs, LED light circuit, and a 120v mini split unit so 40 is enough. I had the 8 gauge wire so I used it. Main question is confirming I need to install a second bus bar for a dedicated ground in the sub panel, correct? I don't bond the neutral bar to the panel either, correct?

    #2
    8 will be good for 50. You need a second ground bus attached to the back can. Take the green screw out of the neutral bus if installed.

    Comment


      #3
      Let me clarify. If the 50 amp breaker's lugs are rated at 75 degree and sub panel lugs are rated 75 degree then you will be good with 8's. I say that strictly as a CYA. All of them are these days.

      Comment


        #4
        If running Romex you are not good, you need a Special

        Comment


          #5
          Just use on a 40 amp breaker and separate the grounds and neutrals in the subpanel.

          Comment


            #6
            Originally posted by KenWood View Post
            8 will be good for 50. You need a second ground bus attached to the back can. Take the green screw out of the neutral bus if installed.
            This

            Comment


              #7
              What type of wire did you run? If it is NM (Romex), it’s only rated for 40 amps. Also, yes you need to separate your neutral and ground bars.

              Comment


                #8
                Thanks all. 8 gauge THHN spooled wire. Got the separate ground bar last night, I'll get it all done up today.

                Comment